December 21, 2012, 01:41 |
Usinf FLUENTs inbuilt function to calculate RH of Moist Air at T_dry_bulb
|
#1 |
Member
Join Date: Jul 2012
Posts: 48
Rep Power: 14 |
Hey guys,
does anyone know which relation FLUENT uses to calculate the RH of moist air at a given temperature? Also can i use the inbuilt formula/method fluent uses to calculate RH at a given temp ? |
|
December 21, 2012, 03:36 |
|
#2 |
Senior Member
SSL
Join Date: Oct 2012
Posts: 226
Rep Power: 15 |
Try more, you can find it...
|
|
December 21, 2012, 10:15 |
|
#3 |
Member
Join Date: Jul 2012
Posts: 48
Rep Power: 14 |
hey there . i found one more realtion for temperature range < 650 k (IAPWS standards) around .. however the results of RH calculation from fluent and IAPWS formulas at a given mf and temp vary too much.
Anyone can plz help .. with what exactly FLUENT does with respect to this? or where Im committing possible errors???: confused: |
|
December 22, 2012, 10:25 |
|
#4 | |
Member
Join Date: Jul 2012
Posts: 48
Rep Power: 14 |
Quote:
i was mistaking mass_fraction used by fluent as humidity ratio! IAPWS formation matches with FLUENTS RH calc within 5% relative error (Given a temperature and mass fraction u calc RH from it).. i guess thats not bad Any better methods suggestion here after are so so welcome gd thnx |
||
Tags |
relative humidity |
|
|
Similar Threads | ||||
Thread | Thread Starter | Forum | Replies | Last Post |
Moist Air | dinis | FLUENT | 3 | October 16, 2023 23:05 |
air bubble is disappear increasing time using vof | xujjun | CFX | 9 | June 9, 2009 08:59 |
Droplet Evaporation | Christian | Main CFD Forum | 2 | February 27, 2007 07:27 |
Hurry!How to simulate mass transfer of moist air? | Yang Bin | FLUENT | 0 | January 9, 2005 07:57 |
moist air density | rafat | Main CFD Forum | 5 | June 13, 2001 22:36 |