Transient heat flow
|
#1 |
Senior Member
---------
Join Date: Oct 2010
Posts: 303
Rep Power: 18 |
I'm totally new to transient simulations. I had a newbie question. I was simulating the air flow inside a power amplifier cabinet which had Fans, Power sources and power amplifiers inside.
The power emanation from the amplifiers is of a transient nature and is described by the following details: Output Power = 200 W Duty cycle: Transient attribute:Gaussian, Total pulse duration: 6400 ms So I see that I need to consider 6400 ms as the total time with a time step of 400 ms. But this is something relevant to a single duty cycle so will it be fine to analyze the heat flow inside the cabinet just for a single duty cycle on these lines. Can some one please suggest me regarding this.
__________________
Best regards, Santhosh. |
|
June 1, 2011, 19:29 |
|
#2 |
Super Moderator
Glenn Horrocks
Join Date: Mar 2009
Location: Sydney, Australia
Posts: 17,870
Rep Power: 144 |
In most electronics heat modelling things of this time scale can be averaged out and the avergae heat load used. So I would average the heat load out and apply a constant heat load. But if you are doing a transient simulation anyway then it is easy to apply the transient heat load.
|
|
June 7, 2011, 13:02 |
|
#3 |
Senior Member
---------
Join Date: Oct 2010
Posts: 303
Rep Power: 18 |
Glenn could you please tell me how to calculate this average heat load. I apologize for raising such novice question but my experience is really too limited in this.
__________________
Best regards, Santhosh. |
|
June 7, 2011, 20:00 |
|
#4 |
Super Moderator
Glenn Horrocks
Join Date: Mar 2009
Location: Sydney, Australia
Posts: 17,870
Rep Power: 144 |
Integrate the heat load over a long time. If it is 11W for 1s and then 1W for 4s, and then repeats that pattern forever, then integrating over the full 5s cycle gives (11*1+1*4)/5 = 3W average load.
|
|
|
|
Similar Threads | ||||
Thread | Thread Starter | Forum | Replies | Last Post |
transient result in spray reactor with swirl flow | glenn creten | Main CFD Forum | 1 | August 14, 2012 06:10 |
Constant velocity of the material | Sas | CFX | 15 | July 13, 2010 09:56 |
Heat Transfer boundary conditions for engine coolant flow simulation | rajuks | Main CFD Forum | 0 | February 15, 2010 10:04 |
Flow around pipes - heat transfer coefficient on the wall of pipe | doodek | Main CFD Forum | 2 | November 23, 2009 09:48 |
time averaged heat transfer in oscillating flow | Matthieu Ubas | Main CFD Forum | 2 | November 5, 1999 15:20 |