CFD Online Logo CFD Online URL
www.cfd-online.com
[Sponsors]
Home > Forums > Software User Forums > ANSYS > CFX

How to define humidity in CFX

Register Blogs Community New Posts Updated Threads Search

Like Tree5Likes

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
Old   November 26, 2013, 07:53
Post How to define humidity in CFX
  #1
New Member
 
Atul Patil
Join Date: Jul 2013
Location: India
Posts: 26
Rep Power: 13
atulpat is on a distinguished road
Hello

I want to carry out thermal comfort analysis in a room using CFX. I also want to define humidity in the room. Dry bulb temperature is 25 deg C and RH is 55% but I don't know how to define such boundary condition in CFX? Please help me.
Thanks in advance.
Kiranmech12 likes this.
atulpat is offline   Reply With Quote

Old   November 26, 2013, 08:18
Default
  #2
New Member
 
Join Date: Apr 2010
Location: Athens, Greece
Posts: 15
Rep Power: 16
sosat1012 is on a distinguished road
If i'm not mistaken you could define your boundaries through mass fractions when it comes to humidity. Check this calculator and use the humidity ratio value (kg/kg)

http://www.sugartech.co.za/psychro/index.php
sosat1012 is offline   Reply With Quote

Old   November 29, 2013, 06:45
Post
  #3
New Member
 
Atul Patil
Join Date: Jul 2013
Location: India
Posts: 26
Rep Power: 13
atulpat is on a distinguished road
Thanks Sosat
I am having psychometric chart but problem is with defining the boundary conditions.
I have considered the fluid as a mixture of Air Ideal gas and Water vapour at 25C. This fluid is then assigned in default domain by considering air ideal gas as constraint and water vapour as transport equation. Here kinematic diffusivity of water vapour is taken as
2.5E-5 (m2/s). Again air inlet temperature, velocity and mass fraction of water vapour are defined in inlet boundary condition. But I am getting higher value of relative humidity. Relative humidity is calculated as follows:
Insert→ Expression→ Pg
Definition = (0.61078 *exp ((17.269*(Temperature-273.15 [K]))/((Temperature-273.15 [K])+273.3[K])))*1000 [Pa]
Insert→ Expression→ Relative Humidity
Definition = (((Water Vapour at 25 C. Mass Fraction/Air Ideal Gas. Mass Fraction)*Absolute Pressure)/((0.622+ Water Vapour at 25 C. Mass Fraction/ Air Ideal Gas. Mass Fraction)*Pg))*100
Insert→ Variable→ RH and in expression set Relative Humidity


Please help me.

Last edited by atulpat; November 29, 2013 at 06:48. Reason: small mistake
atulpat is offline   Reply With Quote

Old   November 29, 2013, 08:41
Default
  #4
New Member
 
Join Date: Apr 2010
Location: Athens, Greece
Posts: 15
Rep Power: 16
sosat1012 is on a distinguished road
If i understand what you say ( i am a bit confused) you cant define the initial temp and RH inside the room? Am I correct?
Well if this is the case you should use initialization. These are not boundaries but initial values of your domain. There you can define initial velocities inside the room and the concentrations of all the gases that are not the one defined as constraint (air for you). It will appear itself to have only water vapor and you can define there the initial RH as a mass fraction.

I hope i helped. If not we could go on brainstorming
sosat1012 is offline   Reply With Quote

Old   November 30, 2013, 02:01
Default
  #5
New Member
 
Atul Patil
Join Date: Jul 2013
Location: India
Posts: 26
Rep Power: 13
atulpat is on a distinguished road
Thanks for reply

Actually I have carried 2 to 3 case studies on thermal comfort in room. But I am getting slightly different results.
Now I am just explaining one case study. A hospital room having one patient and two staff members and one lamp. Initial temp. of room is 20 C so I am considering it as dry bulb temp. and relative humidity is 68%. From psychometric chart humidity ratio becomes 0.01 kg/kg.
Boundary condition are defined as follows
New material: Mixture Air
Basic Setting: Option- Variable composition mixture
Material List- Air Ideal Gas + Water vapour at 25C+ CO2 (Here CO2 taken from import library data as Gas phase combustion )
Then this mixture air assigned in default domain.
Buoyancy model- Buoyant
Gravity- -9.81m/s2
Ref. density- 1.2 kg/m3
Turbulence model- SST
Air Ideal gas- Constraint
CO2- Transport Equation (1.2E-5 m2/s)
Water vapour at 25C- Transport Equation (2.5E-5)

Inlet:- Air temp.: 20C, Air velocity: 1 m/s, Co2 mass fraction: 0, Water vapour at 25C mass fraction: 0.01
Lamp face_wall:- Heat flux: 100 W/m2
Lamp side walls:- Heat Flux: 5 W/m2
Patient_wall:- Temperature: 34 C,
Source:Equation source:CO2.mf:1E-5(Kg/m2s)
Source:Equation source:Water vapour 25C.mf:2.5E-6(Kg/m2s)
Patient Back_wall: Temperature: 34 C
Staff_wall:- Temperature: 34 C,
Source:Equation source:CO2.mf: 0
Source:Equation source:Water vapour 25C.mf: 4E-6(Kg/m2s)
Room Walls:- Adiabatic wall

Here residual target kept as 1E-6 and after 1200 iterations I am getting converged results and areaAve RH for default domain getting as 65%(It is OK as per psychometric chart).
Now problem is that
In results, At inlet of domain RH becomes 81% and areaAve Default domain temperature increased to 24 C. Now If we goes for dry bulb temp. 24 C and 0.01 kg/kg humidity ratio then RH should be 53% as per psychometric chart.
If you knows why I getting such results then please reply. Reply from guest also acceptable. Thanks in advance.

Sorry for long post.
namandoshi likes this.
atulpat is offline   Reply With Quote

Old   December 3, 2013, 00:55
Default
  #6
New Member
 
Atul Patil
Join Date: Jul 2013
Location: India
Posts: 26
Rep Power: 13
atulpat is on a distinguished road
Please somebody help me for this problem.
atulpat is offline   Reply With Quote

Old   December 3, 2013, 03:50
Default
  #7
Member
 
Abdul Afoo Parkar
Join Date: Oct 2012
Posts: 42
Rep Power: 14
A_Prakash is on a distinguished road
1) You are initializing your room temperature at 20 deg.C. After that you are specifying your conditioned air to come into the room at 20 deg.C. That doesn't seem right. You say that Domain temperature has increased to 24 deg.C (which is logical and expected), then what is the point of supplying conditioned air at 20 deg.C?

2) Query the velocity at inlet (ave, areaAve in CFD-Post calculator). Is your BC of 1 m/s enforced?

3) What are room dimensions?

4) Is there backflow?

Last edited by A_Prakash; December 3, 2013 at 03:53. Reason: Added: pt.3 and pt.4
A_Prakash is offline   Reply With Quote

Old   December 3, 2013, 06:42
Post
  #8
New Member
 
Atul Patil
Join Date: Jul 2013
Location: India
Posts: 26
Rep Power: 13
atulpat is on a distinguished road
Dear Sir,
Thanks for reply. Actually I have not initialize to the domain at 20 C. Domain walls are considered as adiabatic. and inlet temperature is given as 20 C.Now I just calculated the heat transfer rate Q using wall heat flux and it is 170.98 W for whole domain. Here mass flow rate is 0.17488 Kg/s (1 M/s) and Cp is 1013.53 J/KgK. Using Energy balance equation, 20.96 C outlet temp is obtained. But in CFD result I am getting 23 C outlet temperature and 23.5 C domain temperature. then is it possible?
Also, Here Domain temperature is increasing up to 23.5 C and water vapour mass fraction is 0.01 Kg/kg. So as per psychometric chart, we should get near to 53% relative humidity but in CFD I am getting it 68%. Also, at inlet portion it is showing 81% relative humidity. We can observe this results in attached images. Is it possible?
Here velocity of the air is 1 m/s.
There is no back flow and dimension are also provided in attached images.

Please give me the suggestions.
Attached Images
File Type: jpg velocity streamlines.jpg (94.8 KB, 118 views)
File Type: jpg Temperature.JPG (52.4 KB, 93 views)
File Type: jpg RH on plane.JPG (55.5 KB, 93 views)
File Type: jpg Relative humidity.JPG (50.5 KB, 85 views)
atulpat is offline   Reply With Quote

Old   December 3, 2013, 10:50
Default
  #9
Member
 
Abdul Afoo Parkar
Join Date: Oct 2012
Posts: 42
Rep Power: 14
A_Prakash is on a distinguished road
Ok. Now, it is clear why you are not happy with the result: You expect a 68% RH as per specified mass fraction at inlet, but model is throwing air at 81%RH.
I am no expert (yet)..but, we can troubleshoot...
First sanity check would be: How is your RH equation expression implemented? Is it giving you 68% RH when mass fraction is exactly 0.01?

Would you mind sharing the model?
A_Prakash is offline   Reply With Quote

Old   December 3, 2013, 17:55
Default
  #10
Super Moderator
 
Glenn Horrocks
Join Date: Mar 2009
Location: Sydney, Australia
Posts: 17,871
Rep Power: 144
ghorrocks is just really niceghorrocks is just really niceghorrocks is just really niceghorrocks is just really nice
With streamlines going all over the place like that I find it very hard to believe that this flow is steady state. You are probably going to have to run it transient to get an accurate simulation as the simulation is bound to flap about.
ghorrocks is offline   Reply With Quote

Old   December 4, 2013, 06:28
Default
  #11
New Member
 
Atul Patil
Join Date: Jul 2013
Location: India
Posts: 26
Rep Power: 13
atulpat is on a distinguished road
Thanks for reply.

@A_Prakash:
with the help of psychometric chart I am calculating the RH. And It is difficult to post model due to large size. RH calculation in CFX-Post as follows:
Insert→ Expression→ Pg
Definition = (0.61078 *exp ((17.269*(Temperature-273.15 [K]))/((Temperature-273.15 [K])+273.3[K])))*1000 [Pa]
Insert→ Expression→ Relative Humidity
Definition = (((Water Vapour at 25 C.Mass Fraction/Air Ideal Gas.Mass Fraction)*Absolute Pressure)/((0.622+ Water Vapour at 25 C.Mass Fraction/Air Ideal Gas.Mass Fraction)*Pg))*100
Insert→ Variable→ RH and in expression set Relative Humidity

@Ghorrocks:

How the transient analysis will increase the accuracy of result? And why Energy balance equation is not satisfied? Previously I worked on HVAC of data center, in such cases energy balance eqn. was satisfied but not in this case.
atulpat is offline   Reply With Quote

Old   December 4, 2013, 06:38
Default
  #12
New Member
 
Join Date: Apr 2010
Location: Athens, Greece
Posts: 15
Rep Power: 16
sosat1012 is on a distinguished road
Hi all! As far as i know CFX does not include RH at results analysis. So you give the expression (as you mention and present above) in order to get RH contours. Right? I guess I am. Why not do a cross checking of the results?

If you try the Water Vapor mass fraction contours (provided by default in cfx results), do you get a result of 0.01 at inlet. If yes then there should be a mistake at the expression definition and then I am afraid the area averaged result could be also wrong (that now seems right).
Actually you should get the 0.01 value at inlet. I am guessing the expression is the problem. When you define a boundary value this value should be there. Like with temperature. You define 20C at inlet and you can see that at the contours you attached. If not then the problem is related to the inlet boundary input which would be strange because you only have to give a single number
sosat1012 is offline   Reply With Quote

Old   December 4, 2013, 08:02
Default
  #13
New Member
 
Atul Patil
Join Date: Jul 2013
Location: India
Posts: 26
Rep Power: 13
atulpat is on a distinguished road
Thanks sosat...

I just did the cross checking of the results for water vapour mass fraction and it shows that mass fraction is 0.01 throughout the domain (refer image). So problem may be in the expression of RH. You knows any method (Expression) for defining the relative humidity in CFX Post? and my second question is that why Energy balance equation is not satisfied?
Attached Images
File Type: jpg mf.JPG (67.8 KB, 49 views)
atulpat is offline   Reply With Quote

Old   December 4, 2013, 10:18
Default
  #14
New Member
 
Join Date: Apr 2010
Location: Athens, Greece
Posts: 15
Rep Power: 16
sosat1012 is on a distinguished road
Some quick calculations with assumptions led me to this type

RH = (Xwv/18)*((Xwv*18+Xair*29)/Pwv-sat)*Pmix*100%

Pwv-sat is the saturated air water vapour partial pressure which is equal to 2.338kPA (you can check it from the psychrometrics)
Pmix is the gas mixture pressure which can be considered almost equal to atmospheric pressure that is more or less 101kPA
Xwv = 0.01 in our case (water vapour mass fraction)
Xair = 1-Xwv = 0.99 constraint (air mass fraction)
Numbers 18 and 29 are Molecular weights for water vapor (ok water vapor's is 18.016) and air

with these values i get an RH=69.27% while psychrometrics result to 69.00%
I checked some other values for Xwv and they provide similar small error. If you need the contours for a presentation or such i guess this would do.

I have a question? Why do you need CO2 in the mixture. There seems to be no CO2 source. Initially it doesn't exist (it's concentration is 0 everywhere). On the other hand you are using air that kinda includes CO2. Anyway there is no reason to include staff you don't need (if i checked your data correctly if do not consider this comment).

As for the energy sorry my friend i am not your energy guy...hehe!
A_Prakash and atulpat like this.
sosat1012 is offline   Reply With Quote

Old   December 5, 2013, 00:37
Default
  #15
New Member
 
Atul Patil
Join Date: Jul 2013
Location: India
Posts: 26
Rep Power: 13
atulpat is on a distinguished road
Thanks Sosat...
I will definitely try to calculates RH as per yours RH calculations. Here CO2 is used for patient
atulpat is offline   Reply With Quote

Old   December 6, 2013, 06:42
Default
  #16
New Member
 
Atul Patil
Join Date: Jul 2013
Location: India
Posts: 26
Rep Power: 13
atulpat is on a distinguished road
Thanks Sosat...
Except Temperature results now everything is OK (i.e. Relative humidity). Your expression is working in CFX Pst. I have used following expression for RH.
Insert→ Expression→ Pg
Definition = exp((20.386-(5132 [K]/T)))*132.29 [Pa]

Insert→ Expression→ Relative Humidity
Definition = (Water Vapour at 25 C.Mass Fraction/18.016)*(((Water Vapour at 25 C.Mass Fraction*18.016)+((1-Water Vapour at 25 C.Mass Fraction)*29))/Pg)*Absolute Pressure*100

Insert→ Variable→ RH and in expression set Relative Humidity


Now, if any anybody knows reason of temperature plot problem then please help me. Here Radiation model is not activated and sometimes I am thinking that due to this only I am getting slightly higher temperature.
atulpat is offline   Reply With Quote

Old   December 30, 2022, 07:47
Default moisture transport
  #17
New Member
 
Ethiopia
Join Date: Sep 2022
Posts: 7
Rep Power: 4
ermiasa100@gmail.com is on a distinguished road
hello every body i am faced a chalnege on moisture transport using CFX in solar cavinet dryer
ermiasa100@gmail.com is offline   Reply With Quote

Old   March 3, 2023, 11:52
Default hello every body i am faced a chalnege on moisture transport using CFX in solar cavin
  #18
New Member
 
Ethiopia
Join Date: Sep 2022
Posts: 7
Rep Power: 4
ermiasa100@gmail.com is on a distinguished road
hello please is there any one need to help me about how to model moisture transport in ansys cfx step by step
ermiasa100@gmail.com is offline   Reply With Quote

Old   March 3, 2023, 20:35
Default
  #19
Super Moderator
 
Glenn Horrocks
Join Date: Mar 2009
Location: Sydney, Australia
Posts: 17,871
Rep Power: 144
ghorrocks is just really niceghorrocks is just really niceghorrocks is just really niceghorrocks is just really nice
You can do a simple model using an additional variable, or a more accurate and complex model using a multicomponent mixture. As long as things stay in the gaseous phase these models are quite simple. Modelling anything involving phase change (ie condensation, dew, icing etc) is much more complicated again - and not recommended for beginners.

I do not have time to write a step by step guide. Have a look in the CFX tutorials on multicomponent mixtures and/or additional variables to see how to set them up.
Opaque likes this.
__________________
Note: I do not answer CFD questions by PM. CFD questions should be posted on the forum.
ghorrocks is offline   Reply With Quote

Old   March 12, 2023, 15:37
Default water vapor transport using ansys CFX
  #20
New Member
 
Ethiopia
Join Date: Sep 2022
Posts: 7
Rep Power: 4
ermiasa100@gmail.com is on a distinguished road
i am developing a solar cabinet dryer using ansys CFX the tempreature distribution is okay but it is faced aproblem when i need to model moisture transport

i am traying to use aditional variabls and expression
ermiasa100@gmail.com is offline   Reply With Quote

Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
HELP----Surface Reaction UDF Ashi Fluent UDF and Scheme Programming 1 May 19, 2020 22:13
Installing OF 1.6 on Mac OS X gschaider OpenFOAM Installation 129 June 19, 2010 10:23
Can I define mutistep reaction mechanisms by CFX? Lixian CFX 0 November 19, 2008 11:43
Add user define monitor in CFX Solver Zaidun CFX 0 April 17, 2006 15:57
How to define STOKES equation in cfx? kerl_liu CFX 1 April 3, 2006 23:54


All times are GMT -4. The time now is 15:29.